water cylinder vent pipe

by DPAGEOK » Sun Mar 04, 2007 1:47 pm

hello
I am going to put my hot water tank( indirect )in the loft next to a combi boiler i am worried about what height the vent pipe should be above the cold water tank as the cold water tank will only be about 12" above the cylinder tank and the water level will be about 36"at the top when full will the hot water in the expantion pipe when hot rise above the level of the cold water tank and cause a problem . :?: :?:

Cpt Nemo
Apprentice
Apprentice
Posts: 12
Joined: Thu Mar 08, 2007 4:49 pm

by Cpt Nemo » Thu Mar 08, 2007 5:34 pm

Hi DPAGEOK

There is a formula for calculating the height that the vent pipe needs to be above the level of the water surface in the cold water storage tank (CWST).

This is 150mm + 40mm for each meter of system height.

System height is defined as the height from the coldwater inlet at the bottom of the cyclinder to the top of the water level in the CWST

Also, PLEASE ensure that your cyclinder if well supported when in the attic as it will have a lot of weight in it when full of water (120Kg +)

Cheers
Jim
PS You can find out more about our Weekend Plumbing courses by going to our advert at the bottom of every project on the website.

thedoctor
Posts: 2530
Joined: Sat Apr 08, 2006 1:15 pm

by thedoctor » Fri Mar 16, 2007 2:12 pm

MANY OF THE ANSWERS TO YOUR POSTS CAN BE FOUND, WITH DIAGRAMS, IN THE DIYDOCTOR PROJECTS SECTION. CLICK HERE www.diydoctor.org.uk/projects.htm

tamz
Apprentice
Apprentice
Posts: 6
Joined: Thu Mar 29, 2007 7:41 pm

by tamz » Thu Mar 29, 2007 9:48 pm

Do you mean conventional boiler? A combi is not normally connected to a cylinder.
Anyway. The height of the domestic expansion pipe doesn't really matter too much. Just put it as high as you can if you are stuck for height. The expansion volume when the cylinder is heated will be taken up by the storage tank, not the expansion pipe. Think of an expansion pipe as a vent pipe (for air) and a safety valve (for overheating).
More important is to use a 28mm feed pipe from the tank to the cylinder. Using a 22mm feed when the cylinder is fitted directly below the storage tank in the loft will almost certainly draw air into the pipes when the taps are run, especially the bath tap.
Another consideration is the height of your feed and expansion tank above the boiler assuming you are not going with a sealed system.
The pipework will need careful consideration if you have low head to avoid problems with the heating system. A sealed system should be your preffered option unless there are other considerations.
Why not just use a combi?