leaking combi boiler
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

6 posts   •   Page 1 of 1
stevep44
Labourer
Labourer
Posts: 2
Joined: Wed Feb 03, 2010 7:56 pm

leaking combi boiler

by stevep44 » Wed Feb 03, 2010 8:09 pm

I have a main 24 he combi boiler which has a leak. the water appears to be travelling passed the fan then floods the burner & eventually blows the pcb ( i have already replaced 2 pcb's ), anyone got any clues why this maybe happening, it's really annoying, cheers.

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Sat Feb 06, 2010 6:05 am

2 PCBs 'cos water and leccy don't get on well, get the leak sorted.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sat Feb 06, 2010 1:16 pm

Repair the leak - lol


The fan is at the top of the boiler, above any water connections, so it is rain water ? or is there an overflow above the flue (outside) that could be leaking - running down the wall and in the flue ?


Vertical or horizontal flue ?


htg

stevep44
Labourer
Labourer
Posts: 2
Joined: Wed Feb 03, 2010 7:56 pm

by stevep44 » Sun Feb 07, 2010 9:34 am

[quote="htg engineer"]Repair the leak - lol


The fan is at the top of the boiler, above any water connections, so it is rain water ? or is there an overflow above the flue (outside) that could be leaking - running down the wall and in the flue ?


Vertical or horizontal flue ?


it's a horizontal flue, i think the water maybe coming from the secondary heat exchanger (think that's what it's called) which is connected to the fan.

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

by DEEARR2 » Sun Feb 07, 2010 6:30 pm

There is a possibility that this may be condensate. Check the condensate flow path is clear through the boiler leading to the trap.

gisago
Apprentice
Apprentice
Posts: 17
Joined: Sat Feb 20, 2010 9:23 am

by gisago » Mon Feb 22, 2010 9:04 pm

Is it sorted yet? You need to get the flue seals checked. If condense is leaking from inner flue into outer flue (air intake) and into boiler it may be a bad or damaged seal, wouldnt be the first time.