Search found 3 matches

by Tim1
Fri Sep 17, 2021 12:37 am
Forum: Electrics Forum
Topic: Earth Bonding to CU or MET?
Replies: 5
Views: 2431

Re: Earth Bonding to CU or MET?

Many thanks Mr White. Understood!
The CU is only around 2 yrs old & has exclusively RCBOs
Does that make a helpful difference?
by Tim1
Wed Sep 15, 2021 11:28 pm
Forum: Electrics Forum
Topic: Earth Bonding to CU or MET?
Replies: 5
Views: 2431

Re: Earth Bonding to CU or MET?

Many thanks stoneyboy. Now, the MET connects to an old, hopelessly undersized iron wire which connects to the incoming mains cable shroud. There's just a (new) single 16mm cable from the CU Earth bar to the MET, nothing else. My electrician advised that when the electric company replace the meter, t...
by Tim1
Tue Sep 14, 2021 9:56 am
Forum: Electrics Forum
Topic: Earth Bonding to CU or MET?
Replies: 5
Views: 2431

Earth Bonding to CU or MET?

I'm having a PV system fitted. The electrician has raised the following issue. He said our oil & water 10mm earth bonding cables should go direct to the Main Earth Terminal, but ours go the CU Earth bar, then 16mm to the MET. Is this is a must? They're not long enough at present. Although I beli...