Thank you for the replies to this.
I realise about the individual run and RCB, so that's sorted. The unit seems to have a max. output of 3.1Kw and the run is in the region of 40 feet.
I'm guessing the 6mm suggestion might be best?
Hi,
I'm installing a steam shower that requires a dedicated cable to the consumer unit. It has to be able to take a full 16amp load when in full flow. What thickness of twin and earth wire is best?
Thanks to anyone who can help.
Peter.
I'm about to renew the ring main in my bungalow (solid floors). Even after splitting the load into two or more circuits, I still have a problem restricting the lengths of cable in each circuit to the required 50 metres. This is because all sockets need to be supplied from above. Is it acceptable to ...