Search found 3 matches

by hiwj
Tue Dec 16, 2008 9:01 am
Forum: Electrics Forum
Topic: Unexplained Earth Fault
Replies: 4
Views: 3227

Eric

I did post on both sites because I wanted a reply quite urgently to be honest (and I thought why not try two different sites).
by hiwj
Mon Dec 15, 2008 10:00 am
Forum: Electrics Forum
Topic: Unexplained Earth Fault
Replies: 4
Views: 3227

Thanks for the explanation. The only reason I thought a ring circuit would be better was so there was an alternative path to earth should a section of cable be faulty. I find it hard to believe that a CU will not treat the fact that there is 115v between earth and neutral as a fault (and switch off ...
by hiwj
Sun Dec 14, 2008 7:59 pm
Forum: Electrics Forum
Topic: Unexplained Earth Fault
Replies: 4
Views: 3227

Unexplained Earth Fault

My 13A sockets are on a radial circuit with a 32A MCB and my cooker is on a seperate MCB (both protected with an RCD). Last week I got a nasty shock and discovered that there was 115v between the earth on my toaster (on the radial circuit) and my cooker. There was also 115v between the neutral and e...