Search found 4 matches

by deskee
Mon May 21, 2007 10:37 am
Forum: Central Heating and Air conditioning and Ventilation Forum
Topic: Heating but no hot water
Replies: 8
Views: 69185

Thank you for the reply, I was 99.99% happy that it was the flow sensor as the terminals were wet and it had a slight crack internally. i did get a new part for about £50.00 + delivery, it came the next day and it was clear that it has been slightly modified (redesigned) as the vertical size is dif...
by deskee
Mon May 14, 2007 9:55 am
Forum: Central Heating and Air conditioning and Ventilation Forum
Topic: Heating but no hot water
Replies: 8
Views: 69185

Thank you for the reply. The boiler and heating are working fine. The diverter valve is also clicking into place.(so i took this to be working). Ive taken out the flow sensor and had a look. There was a bit of muck inside the chamber and the magnet was covered in debris. I cleaned it all up includin...
by deskee
Fri May 11, 2007 8:41 am
Forum: Central Heating and Air conditioning and Ventilation Forum
Topic: Heating but no hot water
Replies: 8
Views: 69185

Thanks for the reply.

There has been no hot water at all no matter what we do, at any time of day or night

The pressure is still ok and the heating comes on fine, just no hot water.

anybody had similar, or know what prob might be???

thanks in advance.
by deskee
Thu May 10, 2007 1:10 pm
Forum: Central Heating and Air conditioning and Ventilation Forum
Topic: Heating but no hot water
Replies: 8
Views: 69185

Heating but no hot water

I have a glowworm 30 Ci combi boiler which has been great since it was installed. but yesterday the hot water stopped running hot and is permanently cold. The boiler pressure has stayed at 1.3 bar and the radiators heat up if i turn the heating on, its just when any hot tap is turned on the boiler d...