Search found 7 matches

by heffs
Fri Nov 02, 2007 6:07 pm
Forum: Electrics Forum
Topic: Unable to reset RCD - Neutral side showing Live.
Replies: 3
Views: 4344

Unable to reset RCD - Neutral side showing Live.

Thanks, both Sparx and Blakey. I found the answer. Disconnecting each neutral in turn at the CU, I found which circuit was faulty and traced it back from there. Even though I was working no where near a socket, whoever wired up the house put in a long (3m) diagonal spur cable into which I put a maso...
by heffs
Sat Oct 27, 2007 6:53 pm
Forum: Electrics Forum
Topic: Unable to reset RCD - Neutral side showing Live.
Replies: 3
Views: 4344

Unable to reset RCD - Neutral side showing Live.

Earlier today, whilst the only electrical item plugged in was a kettle (not being used) and a new radio (switched on) - no fridge, no cooker, no lights on, nothing else - the stand alone RCD tripped, and will not reset. The wiring configuration is as follows: Meter. One pair tails to stand-alone RCD...
by heffs
Fri Jun 08, 2007 4:58 pm
Forum: Electrics Forum
Topic: Cooker Control Unit.
Replies: 2
Views: 3277

Cooker Control Unit

Sparx,

Thanks very much for clearing that up. Sorry for not responding earlier, but been away.

Regards

Heffs
by heffs
Tue Jun 05, 2007 6:52 pm
Forum: Electrics Forum
Topic: Cooker Control Unit.
Replies: 2
Views: 3277

Cooker Control Unit.

Hi, Does any one know whether the regulation that the oven control unit has to be within 2m of the oven relates to max. [b]cable[/b] length or if it's as the crow flies? I'm fitting an oven and electric hob over in an island in the new kitchen. I propose to site the control unit on the wall nearest ...
by heffs
Fri Jun 01, 2007 3:48 pm
Forum: Electrics Forum
Topic: Lighting Circiuts
Replies: 4
Views: 3441

Lighting Circuit

Thanks a lot. Very helpful.
by heffs
Fri Jun 01, 2007 11:19 am
Forum: Electrics Forum
Topic: Lighting Circiuts
Replies: 4
Views: 3441

Lighting Circuits

Thanks, Jeffmo, but one further question: if I decide not to split circuit so I don't use another way in consumer unit, is it OK to uprate the MCB to 10 amp to cope with the extra light points?
by heffs
Thu May 31, 2007 7:09 pm
Forum: Electrics Forum
Topic: Lighting Circiuts
Replies: 4
Views: 3441

Lighting Circiuts

Hi, I'm doing a first fix on a new extension, which will be tested and certificated by a qualified electrician (has to be anyway, since Building Control is involved) and have a question regarding the lighting circuit. I'm using 230v halogen downlighters in kitchen, and have a three gang switch contr...