Topic: Blagdon Powersafe kit connection problem
Replies: 6
Views: 7229

Thanks everyone - that was a great help!
by daveace
Fri Apr 15, 2011 12:22 pm
Forum: Electrics Forum
Topic: Blagdon Powersafe kit connection problem
Replies: 6
Views: 7229

Use a connection box that a swa glad can be used with using the earth washer with tag to enable earthing of the steel wire on the swa cable. Dont use one of the tubular connectors as you will loose earth continuity on the steel wire of the armoured cable. OK, that's great! I understand how to cut t...
by daveace
Thu Apr 14, 2011 11:36 am
Forum: Electrics Forum
Topic: Blagdon Powersafe kit connection problem
Replies: 6
Views: 7229

Blagdon Powersafe kit connection problem

Hi folks, I have the Blagdon Powersafe 20m kit (Google "blagdonthepondmasters.co.uk/objects/pdf/Power_Leaflet.pdf") installed in my garden but recently I noticed the RCD was tripping, and I have discovered rain is getting into the connection between the regular 3 core flex and the armoured...