Search found 2 matches

by Argos69
Wed Mar 21, 2012 10:54 am
Forum: Electrics Forum
Topic: Electrical Supply to 2 Outdoor Buildings
Replies: 2
Views: 2135

Re: Electrical Supply to 2 Outdoor Buildings

Hi ericmark & thanks. Since posting, I have now borrowed a copy of the regs and found buried in 433.3.1 (i), a bit which says I can drop the cable size, so long as the protection back at the house is suitable for the smallest cable size in circuit, which it is. That means I can keep the 16A and ...
by Argos69
Tue Mar 20, 2012 5:33 pm
Forum: Electrics Forum
Topic: Electrical Supply to 2 Outdoor Buildings
Replies: 2
Views: 2135

Electrical Supply to 2 Outdoor Buildings

Hi, I hope someone can advise on this one. I have an existing garage which has a 4mm SWA cable supplying a 2 way RCD board (6A & 16A ways) from a 20A MCB in the house consumer unit. I have built a shed which has very little requirements in terms of electricity, but I'd like to feed it from the t...