In the 17th Edition there are two references to proximity to water pipes. In both cases it is the heat produced that is the problem. The exact solution you need to work out this could of course include the use of cables more able to stand the heat the heat of the cables would need measuring and reference to table 4B1 will show the de-rating factor to be used. The max temp for standard twin and earth is 60°C but low smoke cable could run at 80°C but at those temperatures cable sizes would need to be double that used at the standard 30°C. I don’t have an old 16th Edition to hand but I would not think there has been any great change.
522.2.1 In order to avoid the effects of heat from external sources, one or more of the following methods or an equally effective method shall be used to protect it wiring system:
(i) Shielding
(ii) Placing sufficiently far from the source of heat
(iii) Selecting a system with due regard for the additional temperature rise which may occur
(iv) Local reinforcement or substitution of insulating material.
528.3.1 A wiring system shall not he installed in the vicinity of services which produce heat, smoke or fumes likely to be detrimental to the wiring. unless it is protected front harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring.
In areas not specifically designed for the installation of cables. e.g. service shafts and cavities, the cables shall be laid so that they are not exposed to am harmful influence by the normal operation of the adjacent installations (e.g. gas. water or steam lines).