earth bonding
All aspects of plumbing questions and answers, help, tips and information

4 posts   •   Page 1 of 1
paul pearson
Apprentice
Apprentice
Posts: 5
Joined: Tue Jun 24, 2008 10:22 am

earth bonding

by paul pearson » Tue Jun 24, 2008 10:26 am

hi just wondering where the best place is to pick up the earth bonding is it ok from a light socket

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Tue Jun 24, 2008 7:42 pm

Absolutely definitely not!

Earth bonding (assuming a domestic property) must be 10mm cable directly earthed at the consumer unit.

Apart from the huge difference in the cable size if the lighting circuit were to develop a fault, it is conceivable the metal you intend to bond may become live.

What exactly are you bonding?

It would be better to post an electrical question to the electrics forum rather than the plumbing forum.

paul pearson
Apprentice
Apprentice
Posts: 5
Joined: Tue Jun 24, 2008 10:22 am

by paul pearson » Wed Jun 25, 2008 9:51 am

it was just the pipe work on a sink but will not bother will get somebody in



cheers

bobplum
Foreman
Foreman
Posts: 364
Joined: Tue Sep 25, 2007 8:35 pm

by bobplum » Wed Jun 25, 2008 8:13 pm

hi on the assumption the piping is bonded were the mains come into the house you only need to cross bond across the pipes
bob

4 posts   •   Page 1 of 1
It is currently Sun Sep 29, 2024 12:21 am