The rules on RCD’s look at a number of reasons which they should be fitted.
1) All sockets under 20 amp and all electrics in a bathroom.
2) Wires buried at less than 50mm and not protected.
3) Fire.
4) Earth loop impedance.
First two are 30ma and this is maybe be over simplified and there are also rules as to splitting supplies which have resulted in multi RCD’s being fitted in most cases.
Since to fitting of consumer units also comes within Part P it is unlikely any DIY work would be worth while by time LABC charges are taken into account.
You ask what it leaves out and in the main either surface wiring or one of the permitted cables would need to be used i.e. Flexishield. Using this type of wiring sockets marked for the use of a specific item i.e. Fridge/Freezer, Cooker, Immersion heater, Smoke detectors will not need RCD. Lights with exception of bathroom will not need an RCD.
The main problem is most houses have cables buried in walls which do not comply with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436 so although the smoke detector does not require an RCD the wiring feeding it does, and also safety circuits can’t use same RCD as sockets etc so a RCBO would be required.
Most BS 8436 also complies with FP200 so fire protection circuits with BS 8436 cable would make sense. As yet the BS 8436 has not really caught on so not so easy to source but I am sure that will change soon.
Remember I have not included all factors like earth loop impedance for example but anyone fitting a consumer unit would need to fill in the installation certificate and should know all of this anyway. A copy of the certificate will be found I think page 23 of Part P document a link to that will be found in Projects section.
Many consumer units now have three neutral bars two for use with RCD’s and one for RCBO’s used on smoke alarms and the like or where cable to BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436 is used.
Yours Eric