Back Boiler and room ventilation
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

4 posts   •   Page 1 of 1
greengiant57
Labourer
Labourer
Posts: 2
Joined: Sun Sep 28, 2008 5:55 pm

Back Boiler and room ventilation

by greengiant57 » Sun Sep 28, 2008 6:07 pm

I have a gas fired back boiler unit behind a flame effect gas fire, situated in the lounge of my 1970's home. At the last boiler service, the engineer said that the system would not be covered in future years, as the air brick installation in the lounge wall did not conform to the current regulations.
Apparently I need to install a cavity wall liner.

Can anyone offer any info or advice?

Are these off the shelf items, available from builders merchants or DIY stores? Are they difficult to fit? Do they have to conform to any regulations.

I have a lot of questions regarding these, so any help would be much appreciated.

Thanks,

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Mon Sep 29, 2008 5:31 am

Hi,

You need an air brick/vent to the outside world of 100cm2.
Stadium do such a vent -> 5" hole, tube, 2x vent covers - job done.

Hth

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Mon Sep 29, 2008 7:34 am

You can buy plastic air bricks (sometimes referred to as black holes) with the plastic sleeve between the inner and outer vent.


htg

screech
Ganger
Ganger
Posts: 56
Joined: Tue Sep 02, 2008 10:51 pm

by screech » Fri Oct 03, 2008 12:26 am

if you get a vent like already suggested you'll be fine but if you go for another one not sleeved make sure it can't be closed and it mustn't have a flyscreen either.