help

by heating09 » Fri Mar 06, 2009 2:57 pm

oil boiler on balanced flue

increase the air on the burner to obtain the correct combustion reading

but increasing the air seems to blow the flame out

any suggestions on how to remedy or why this happens

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Sat Mar 07, 2009 4:33 am

Hi,

Your getting flame lift - too much air.
Are you qualified?
If not, get an Hetas person in?

stoneyboy
Project Manager
Project Manager
Posts: 6546
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Sat Mar 07, 2009 5:07 pm

heating09,
The equipment you are using to test the combustion gases is giving the wrong reading.
end

heating09
Labourer
Labourer
Posts: 3
Joined: Fri Mar 06, 2009 2:53 pm

by heating09 » Sat Mar 07, 2009 9:42 pm

yes qualified, why is the flame blowing out????

nothing to do with meter,

had to leave it burning rich with high co

why cant i increase the air with out it tripping out

nozzle may be ???

any suggestions

stoneyboy
Project Manager
Project Manager
Posts: 6546
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Sun Mar 08, 2009 4:25 pm

heating09,
Have you checked the pressure to the nozzle, is it set as in the operating manual? Have a look in the manual and see what nozzle is recommended. If you are using a hollow pattern nozzle, try a solid one and vv.
When you now refer to "tripping out" do you mean this or that the flame becomes unstable and blows out.
end

heating09
Labourer
Labourer
Posts: 3
Joined: Fri Mar 06, 2009 2:53 pm

by heating09 » Mon Mar 09, 2009 8:12 am

nozzle pressure ok

flame begins to blow out every 5 mins or so when correct co2 is reached

flame only stabilises when burning rich i.e 13% co2

this isnt any good cause the co then goes to 300ppm

stoneyboy
Project Manager
Project Manager
Posts: 6546
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Mon Mar 09, 2009 9:24 pm

heating09,
Have you tried a new nozzle? Is the correct size nozzle fitted ie one which matches the boiler. Check the manual and see if the burner has been replaced with one which is too big for the boiler. Have you checked the relationship between the nozzle and the air spinner plate does this match the spec in the manual?
end