by sparx »
Mon Apr 13, 2009 10:13 pm
wws4029,
What you have is a fault between line & neutral on 230V circuit 10 on dist.bd. 1.
If as you say it is supplying an immersion heater from a 32A mcb then it should be either a 4mm2 cable or the mcb should be 16A.
Unfortunately both LINE & NEUTRAL conductors are now refered to as 'lives', however the inspector is quite wrong to call it a phase to phase fault.
hope this helps,
one other thing, if there is a fault the circuit will trip, it may just have a low insulation resistance reading, which is not unusual on water heaters, look for the readings on the test sheet, an IR reading of over 0.5M.ohms will normally allow the heater to still work!
regards SPARX