SHOWER TRIPPING
aldino
SHOWER TRIPPING
by aldino » Mon Nov 30, 2009 12:26 am
HI,MY 9.5KW TRITON SHOWER IS TRIPPING MY MCB WHEN ITS ON THE SECOND HEAT SETTING.ITS FINE ON THE FIRST HEAT SETTING.IT WORKED FINE FOR MONTHS BUT NOW ITS TRIPPING.ANY THOUGHTS.
moggy1968
by moggy1968 » Mon Nov 30, 2009 10:16 pm
what rating is the mcb?
aldino
by aldino » Tue Dec 01, 2009 8:07 pm
50AMPS
by sparx » Wed Dec 02, 2009 6:50 pm
50A mcb should never trip on a 9.5kW load, it will carry 11.5kW for ever!
Is it just an mcb or is it an rcbo? If so it could be tripping due to earth leakage from failing element.
btw would love to know the cable size to your shower 'cos unless its surface clipped the whole way it must be bigger than a 10mm2!
All other methods of installation would leave the cable unprotected by a 50A mcb, 9.5kW should only need a 40A mcb.
Only other thought is to get the running current checked with a clip on ammeter, if less than 50A then mcb could be faulty, or since mcbs are so inexpensive assume it's duff and get it changed anyway, then if still trips shower fubar'ed,
regards SPARX
(Usual comments ref work in bath/shower rooms & consumer units ref 'Part P')
aldino
by aldino » Wed Dec 02, 2009 7:38 pm
HI,THANKS FOR THE INFO.I THINK THE SHOWER IS THE PROB BECAUSE THE CABLE IS 10MM AND THE MCB IN THE CONSUMER UNIT SHOULD BE ENOUGH.I WILL CHECK THE WIRING TO SEE HOW TO IS ROUTED.