by ericmark »
Thu Apr 08, 2010 1:38 pm
What I was trying to say
For earth loop impedance then supply limit i.e. D16 MCB is what you go by.
For volt drop it is actual use.
However since electricians often don't have control of use then often we still go by MCB size.
However if it were for example supplying a HF florescent unit in a shed, and only that, and the unit gives a input voltage of 100 - 240v AC/DC, then to say the volt drop must be limited to 3% is daft.
And yes the ELI must be lower than the amount which would allow it to trip.
So calculation C type = x10 so max current = 160A @ 230v that's 1.4375 ohms max so assuming 0.35 (PME) on incoming supply you have 1.0875 ohms so around 6.17 meters is max length of a 4mm supply.
But you want to use a 1.5mm earth and that will give max of around 4.26 meters unless a RCD is used.
Use a B16 and your up to 9.894 meters
Use a B10 and your up to 16.65 meters
Use a B10 and 4mm for earth and up to 24 meters
Use a B10 and 6mm for earth and up to 36.38 meters
Now on a 35 meter run you are unlikely to use twin and earth much more likely to be SWA and if you use 3 core then both the SWA and the core can be used for earth and now with a B10 and 4mm you are likely to be able to get the readings required however since the SWA cross sectional area varies between makes I can't calculate the value.
Sorry to say it is not that easy in real terms as one does get parallel earths and it is the meter reading that matters.
Using a TT system you may have better results this will need RCD protection and as I said it depends on location you may have to use a TT system anyway.
Electrical installations outdoors: a supply to a detached outbuilding in Wiring Matters (Google "theiet.org/publishing/wiring-regulations/mag/2005/index.cfm") does go through all the ins and outs but do remember this was pre 2008 so there will be some changes to comply with BS7671:2008