Hi, SWA /PVC 6mm 'clipped direct' on surface is rated at 49A, on a metal cable tray or 'in free air' is 53A, so your supply end MCB would have to be no larger than a 45A unit.
If using SWA/XLPE insulation then figs become 62A &66A respectively, so could use 60 A fuse or just abt.63A MCB.
Assuming the latter, the max load on system would be 30A max due to excess volt drop over the distance, so in fact a 32A mcb /rcd combination would be sufficient, fitted at supply end (house) with the lights fed from a fused connection unit (Fused-Spur) from ring.
To achieve your max load would need a 10mm2 cable, hope this helps, regards SPARX