Hard wiring rangemaster classic 90
lona
by lona » Wed Jan 12, 2011 5:31 pm
When connecting a dual fuel Rangemaster can the cable be hard wired directly into the consumer control unit.?
collectors
by collectors » Thu Jan 13, 2011 9:53 am
You should always have a form of local isolation in the way of a switched fused spur or even a simple wall socket with a plug if its a boiler & an appropriate sized switch & fuse if its a cooker.
kbrownie
by kbrownie » Thu Jan 13, 2011 5:50 pm
The appliance should be on it's own circuit, but a direct conection between the applainace and the CU, must not be made. As you will need a cooker control unit to give you an easy means of isolation, this should be installed within 2 metres of the appliance, ideally in a visable location like above the worktop.
If the circuit is a new circuit, it is very likely a RCD/RCBO will also need to be installed (if your CU is not already fitted with this) as additional protection, this will by deemed notifiable work to building controls.
by ericmark » Thu Jan 13, 2011 9:36 pm
I have looked up the Rangemaster 90 and some of the ratings are a surprise. The hob is rated higher then whole cooker but 10.9 kw is 47A and with the induction model that drops to 9.7 kw so I have a feeling some one has got their figures mixed up!
3 x 2.3kW, + 2 x11.4kW = 9.7kW I know my maths is bad but not that bad!
Anyway I would get the real spec out and work out what it really needs.
Clearly the manufacturer can't be trusted and common sense needs to prevail.
It is currently Thu Jan 16, 2025 2:50 am