just to clarify are you putting 2 8,5kw showers on the same mcb?
if you did that the combined load would be clse to 74 amps so that is a big no no,
you can put them on seperate breakers but you have to consider the total load in the rest of the property, as if you only had a 60amp main head fuse and then put both showers on you would have problem.
Assuming you have a 100amp main head fuse then you have amps to play with so to speak but you wouldnt want to be putting the fuse to its limits, also showers should be on an rcd and they normally are rated to 60amps thus creating a problem straight away with both showers on.
Probably better to use the showers individually on differnt correctly rated breakers, 37amps with 8.5kw use 40amp breaker