Wall Thermo stat
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

3 posts   •   Page 1 of 1
gel
Apprentice
Apprentice
Posts: 16
Joined: Mon Feb 18, 2008 3:47 pm

Wall Thermo stat

by gel » Sat Oct 08, 2011 6:19 pm

I have recently moved into a house which has full gas central heating
All the radiators are fitted with thermostatic valves with the exception of the hall radiator
The wall thermostat is positioned in the hall
If I set the wall thermostat at say 18 which should be sufficient for the hall should be able to get a higher temperature say 21 in a living room
Thank you for any comments
gel

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Re: Wall Thermo stat

by sparx » Fri Oct 14, 2011 4:53 pm

Hi, short answer No, when hall gets to 18 it will shut boiler down.
The system as set up complies with building regs. the hall is used as a cut off point to save boiler cycling.
The hall rad should be very small in comparison to the others so other rooms should be up to temp. before hall is, then as ARV's shut supply to each rad the flow will go up in hall.
The main benefit of having a stat. is that if the timer tries to operate the boiler on a day when 'solar-gain' has already raised the house temp. above its set point the boiler doesn't fire unnecessarily

gel
Apprentice
Apprentice
Posts: 16
Joined: Mon Feb 18, 2008 3:47 pm

Re: Wall Thermo stat

by gel » Sat Oct 15, 2011 10:28 am

Thank you very much for your reply It is most helpful
Cheers