I read, then re-read, and tried to think of a reason for running two parallel cables, I will guess it was intended to extend the ring, and for some reason they changed their mind.
Only reason I can think of is the loop impedance was too high, and I can't think of an easy way for you to test.
Anyway nothing wrong leaving it as it is, I was told when doing inspection and testing course we should test for a figure of 8 which is what you have, but as I studied further I could not see any real problem with it.
So with modern regulations we are permitted 108 meters of cable in the ring, it was 80 some thing, and the reason limited is volt drop, there is another reason to limit length which is the earth loop impedance, however with RCD protection that is not so much a problem.
So likely there is no reason why you can't remove one cable, but without some readings can't be sure. If RCD protected then having over the permitted volt drop is not that much of a problem, fridges and freezers can be damaged by excessive volt drop but very little else.
Have you got a schedule of test results either part of installation certificate or electrical installation condition report? If so that should tell us how close it was to the limit.