mains smoke Alarm
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
Basil20
Apprentice
Apprentice
Posts: 12
Joined: Sun Apr 08, 2007 1:50 pm

mains smoke Alarm

by Basil20 » Sun Apr 08, 2007 2:05 pm

I wonder if anyone can help me
I want to fit a mains smoke alarm with battery back up in my house
and wonder if it can be feed from the lighting circuit, and if so can i take another smoke alarm looped from the first one.
[/u]

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Apr 08, 2007 11:08 pm

Yes & yes,
find perm. live & neutral at nearest light, use twin/earth to first alarm, loop between alarms using 3core /earth.
this supplies power to second alarm & third wire is trigger so whichever alarm goes off they both(all) sound, together.
regards Sparx

Basil20
Apprentice
Apprentice
Posts: 12
Joined: Sun Apr 08, 2007 1:50 pm

by Basil20 » Mon Apr 09, 2007 10:49 am

Thanks for your help Sparx

Jeffmo
Ganger
Ganger
Posts: 103
Joined: Mon Apr 09, 2007 10:22 am

by Jeffmo » Mon Apr 09, 2007 11:08 am

All lights on one circuit , all sockets on one radial circuit is this okay or do i have to split them both to upstairs and downstairs?

4 posts   •   Page 1 of 1
It is currently Wed Nov 27, 2024 7:56 pm