Hi , main earth bonding must go from your consumer unit to water main stop cock on house side within 300mm of it, the gas also has to go to the gas meter from consumer unit to house side of meter.
If meter is indoors then you must connect to fixed not flexy pipe within 300mm, before any branch or tee, If meter in out door box you may connect inside within 300mm of point of entry.
The only variation is if the route to one service goes near the other one it is permitted to loop your bonding wire from the Con. unit to first one then the other but the wire has to be continuous un broken ie a section of insulation removed at first earth clamp, wrapped around screw and carries on to end at other service.
Hope this makes sense,
N.B. cable must be 10mm2
Regards SPARX