Gloworm Lifestyle LP241 Problems

Posted: Mon May 19, 2008 8:05 am
by bm2008
Hi,

We have a Gloworm Ultimate Central Heating System that has a Lifestyle LP241 control panel, having problems... not sure if anyone can help?

You can turn the water and heating on and off independently using the control panel. At the moment it is switched to only heating the water. BUT it is also heating the radiators as well.

We have had the valve replaced in the boiler but that has not fixed the problem.

Has anyone else had this problem?

Thanks in advance.

Posted: Mon May 19, 2008 9:00 pm
by htg engineer
You've had the valve replaced in the glow worm ultimate ??
What valve.

It will be the three port valve or motorised head at fault. There's no diverter or motorised valve in the boiler.

This will be near the pump near the boiler or in the loft or siring cupboard.

Hope this helps

htg

Posted: Mon May 19, 2008 11:19 pm
by bm2008
[quote="htg engineer"]You've had the valve replaced in the glow worm ultimate ??
What valve.

It will be the three port valve or motorised head at fault. There's no diverter or motorised valve in the boiler.

This will be near the pump near the boiler or in the loft or siring cupboard.

Hope this helps

htg[/quote]

Replaced the valve in the boiler! sorry to confuse you!
Many thanks for your help, the valve was replaced in our airing cupboard tank... a few weeks ago. But the problem has come back...

Posted: Wed May 21, 2008 7:31 pm
by htg engineer
Threee port valve or actuator at fault, check again.

The actuator has been changed, fitted properly ?
Check the valve, turns freely ? possibly new valve required.

htg