Heating on Hot Water only but pump continues to feed heating
Posted: Thu Aug 14, 2008 3:48 pm
by DigsySE18
My boiler is programmed to heat the water only twice a day. During those times the central heating pump comes on as well and pumps water through the rads. The sound of water pumping round the system is very noisy. How do I stop it???
Posted: Thu Aug 14, 2008 4:56 pm
by htg engineer
Type of system ?
make and model of boiler ?
Posted: Thu Aug 14, 2008 7:58 pm
by DigsySE18
Hi. Itrs a Potterton Suprema 30-80, wall mounted fan assisted balanced flue gas boiler
Posted: Fri Aug 15, 2008 7:27 am
by htg engineer
There'll only be one pump and a 3 port valve, check the 3 port valve and actuator - it's probably the actuator that is faulty.
htg
Posted: Fri Aug 15, 2008 9:15 am
by AdamsHeating
Hi,
5-1 favourite to be the actuator, it always is.
I might move into research on the production of an infallible actuator, what do you think htg engineer, split the profits, there is bound to be some!?