Radiators constantly need bleeding
Posted: Fri Oct 31, 2008 7:40 pm
by stuy180
My great aunt's radiators are constantly cold, you can bleed them on one
day and the following day they need doing again.
She's had a heating engineer round today who's told her that her hot water cylinder is drawing air in and she needs a new one. The problem is he's also told her she needs a complete new system....to the tune of 15k!
The heating engineer didn't tell her this until my Dad had left... :roll: my great aunt is 101 and this has really worried her and doesn't seem to ring true to me. Surely she would only need a new cylinder? :?
Posted: Fri Oct 31, 2008 11:55 pm
by plumbbob
Sounds a little suspicious to me too, but I cannot offer any advice without having information about what type of system it is.
Obviously, we cannot see your system so cannot simply dismiss your plumber's comments, but usually systems repeatedly filling with air are caused by bad design, and the fault has no connection with the hot water cylinder.
Posted: Sat Nov 01, 2008 7:58 am
by Steve the gas
Is your great aunt the Queen? 15k for a new system WTF
Posted: Sun Nov 02, 2008 2:02 pm
by stuy180
Ok from what I can make out from looking today, its an in direct sytem.
The engineer fitted a new pump while he was there because apparently the old one was to small (The old one only being a year old) The new (Bigger) pump thats been fitted is on the lowest setting.
If the smaller pump was set on No 2 or 3 but the bigger one is set on No 1, would this be any different?
I also noticed that the stop valve on the heating return (I believe) within the airing cupboard was turning but not stoping (Valve stuck)?
The pipe running through this valve was warm but no where near as hot as the flow, the radiators seemed like they were hot at the top but cold/warm along the bottom.
If the stop valve is jammed could this be the reason for the radiators not perfoming as they should?
Would it be better to replace the stop valve and see what happens?
Apparently my father inlaw has heard the air valves in the loft working as they should not so long ago and all the radiators are full (No air).
Any advice muchly appreciated!
Thank you
Heating/Hot water cylinder
Posted: Sun Nov 02, 2008 2:49 pm
by stuy180
The system is indirect. The engineer has replaced the pump because apparently the old one (a year old) was too small, if the old pump was set at 2 or 3 and the new one is set at 1..... Would this be any different?
If the new one is set any higher, water starts coming from the overflow out of the roof.
I bled all radiators today but there was no air, just water. They were also all hot at the top but cold/warm at the bottom.
I noticed that the stop valve on the heating return (I believe) within the airing cupboard is not working as it should, the head would just keep turning. The flow was very hot but the return was cold/warm, would this be because the stop valve is stuck/jammed?
Would this also possibly be the reason for the radiators not working as they should and the hot water being hotter than normal?
If the valve is not working properly, the flow of the heating system is not working as it should, if its not flowing the way it should would the heating pipe running within the hot water cylinder get hotter than normal or flow slower therefore heating the hot water thats already within the cylinder?
Does it sound like there is a problem with the cylinder IE: A leak drawing air into the heating system like the engineer has said?
Should I just get the stop valve replaced and see where it gets us?
Also..... Would it of taken a day for two engineers to figure out a leak and not find the tap jammed?
Thank you so much for you replys
Any advice/help is appreciated.
Posted: Sun Nov 02, 2008 9:58 pm
by plumbbob
Unfortunately, there are several different types of indirect system and without knowing which type it is, there is only so far we can go with advice.
If there is air constantly being drawn into the system, fitting a bigger pump may exacerbate the problem.
If radiators are cold at the bottom and hot at the top, this is caused by insufficient flow of hot water. So if you have a new bigger pump, and still no circulation of water, where is it going? Well, there are several options. Firstly, is all the water circulating just some of the rads and failing to reach others? Try balancing the system (See projects section on how to do this).
Secondly, and probably more likely, a bypass valve has been left fully open, or the cylinder lockshield vale is fully open. So the water is simply taking the easiest route and avoiding the heating circuit.
You need to google sundial plans (honeywell is a good site) and describe which plan is closest to your design.
As for the valve, well that's how they break. Just turn, and nothing happens. It could be shut, open or in between. Trouble is, without knowing exactly where it is in the system, it is difficult to tell what it is supposed to do. It may need adjusting, so does need to be replaced.
Symptoms of a faulty cylinder are discoloured hot water from the taps, and overflowing central heating header tank. (The tank overflow to outside not the expansion pipe) AS you have not mentioned either, I would not point the finger at a fault here. Cold rads does not indicate a cylinder fault either.
It took a day to change a pump (unnecessary?), fiddle about and come to a suspect decision? Frankly, I would be wary. As I said though, I cannot condemn anyone as I cannot see the system.
Heating
Posted: Mon Nov 03, 2008 11:54 am
by stuy180
If the pump is turned any higher than the first setting, water comes from the overflow in the roof.
I have tried balancing the system already, this didn't work.
If the stop valve is closed or almost closed, would this be the answer for the hot water flow around the rads (possibly)?
I know it seems like I keep repeating my self but for me to keep going and looking at the system, its almost an hours drive away. :(
Posted: Mon Nov 03, 2008 6:24 pm
by plumbbob
The overflow from the expansion pipe into the header tank is caused by a badly designed system. Turning the pump speed up will increase the pressure differential in the system and consequently, make the fault worse. Although this needs to be rectified, it is not causing poor flow of water around the system.
Stop valves (or rather gate valves with red handles?) found in airing cupboards have two possible functions. If the tap is at about chest height and the pipes in which they fix disappear into the loft, thy are most likely isolation valves used to shut off the different flows and should be fully open.
If the valve is lower down and fitted in the heating circuits they are most likely being used as restrictor valves and will normally only be very slightly open (or maybe even shut if it's an unrequired bypass). Opening these valves too far will unbalance the system and stop the water from flowing around the rads.
Of course another possibility with the overflow and trapped air problem, is oxygen will be drawn into the system and cause it to rust and the resulting sludge can build up and restrict flows.
heating
Posted: Tue Nov 04, 2008 12:47 am
by stuy180
OK,
Thank you for the advice, I am hoping to get out there on Wednesday.
I will see what I can do.
Thanks again! :D
Heating
Posted: Tue Nov 04, 2008 5:09 pm
by stuy180
I have just found out that when the engineer was round trying to solve the original problem and fitting a new pump (that was not needed)
He charged my great aunt (101 yrs old)
OVER £700 for installing the pump!
WTF is that all about?
Posted: Wed Nov 05, 2008 5:54 am
by Steve the gas
Mate do not use these rip off merchants. Find another by recomendation.
New pump fitted approx ( if standard) £100 - £150
Heating
Posted: Wed Nov 05, 2008 5:25 pm
by stuy180
Ok, I changed the isolating valve by the hot water cylinder today.
The valve was almost closed completely, the rads are now getting hot both top and bottom.....
there are 2 rads not getting too hot, I noticed the return valve and pipe was getting hot before the flow on these 2 rads....... would this be why?
what should be done with these?
Thank you so much Gents! :o and Ladies? :? maybe.
Posted: Wed Nov 05, 2008 9:17 pm
by plumbbob
Steve is right on price. You GA has been ripped off big time!
You should have the system checked by a recommended repair engineer and take further action!