combi boiler heating water but not rads

Posted: Sun Nov 23, 2008 11:51 am
by JOATMON
Hi , we have a Raven heat boiler ,the water heats up but not the rads , ,Ive replaced a thermo valve , but the heating worked for weeks after that , Ive bled the rads and lots of air came out of them but still no joy AND NOW ITS SNOWING !! can you help please ?

Posted: Mon Nov 24, 2008 7:42 pm
by JOATMON
Its still snowing and i cant get a plummer ( im just a daft joiner )

Posted: Tue Nov 25, 2008 5:38 am
by Steve the gas
Hi,

Do you have a dripping hot tap, and I mean even slightly?

Diverter valve is where I would begin


Hth

Posted: Tue Nov 25, 2008 10:44 pm
by gasmick
Its a problem with the electronic timer on the front panel even if the red light is on it does not switch over inside so it needs it can be bypassed
on a temp thing as the contacts are volatage free, and just need looping together, get a corgi man to do a temporary link so at least you will have the heating working
you do not say which model it is by the way but the all use the same digital clock
i have replaced dozens
the diverter valve sit on the heating in an open position and the port is only closed on a call for hot water

Posted: Wed Nov 26, 2008 10:44 am
by JOATMON
Thankyou all very much for your help , ill give your ideas a go and let you know how we go cheers

Posted: Thu Nov 27, 2008 12:53 pm
by JOATMON
it was the clock :D
Corgi guy came out bypassed the clock and ordered a new one £68 thanx for your advice 8)