Posted: Wed Nov 26, 2008 9:02 pm
by tfella
My radiators are cold at the bottom yet warm at the top. This problem is usually the opposite way round so do they just need bleeding?

Posted: Thu Nov 27, 2008 11:03 pm
by AdamsHeating
If you bleed and they are full you probably have a blockage/sludge build up. Might need a cleanser running through it or power flushing.

Posted: Thu Nov 27, 2008 11:06 pm
by Loffa
If its an old system it probably needs a powerflush or at least taking the rads off and flushing through individually. They are more than likely sludged up.

Posted: Fri Nov 28, 2008 5:39 am
by Steve the gas
Hi Fella,

Cold at top = air, therefore bleed.
Cold at bottom = sludge or circulation problem, therefore powerflush or diy drain down flushout several times then add inhibitor.


Hth