Very noisy boiler
Posted: Sat Nov 29, 2008 7:17 pm
by Edpaterson
My boiler is 7 years old (a HENRAD 50FF) and seems to have developed a very annoying buzz when it is on. The buzz seems to be to be close to the 50Hz buzz which sometimes come with electronic equipment. Any suggestions as to how I might reduce this?
Ed Paterson
Posted: Sun Nov 30, 2008 2:26 pm
by htg engineer
Firstly you need to find where the noise is coming from - check solenoid on gas valve.
htg
Noisy boiler
Posted: Tue Dec 02, 2008 1:17 pm
by Edpaterson
Hi
Thanks to htg engineer for his response. I have checked out the boiler and it does seem as if the noise is coming from the solenoid valve. When I restrain the coil the noise is reduced. Is there a permanent fix for this problem?
Ed
Posted: Wed Dec 03, 2008 4:53 am
by Steve the gas
Yes Ed new solenoid.RGI job
Very noisy boiler
Posted: Thu Dec 04, 2008 8:48 am
by Edpaterson
Hi
Thanks to both Steve and htg engineer for their advice. I shall now enter the jungle to find a reliable CORGI registered heating engineer.
Ed