ineffective heating - (repost)
Posted: Mon Jan 19, 2009 12:20 am
I have been advised to re-post this topic:
I have just moved into a new built house and the heating seems ineffective so if any heating engineers could offer their opinion i would be very grateful:
House is 3 storey with 2 heating zones both controlled by thermostats one in hallway and one on 1st floor.
System is basically all working as it should, all rads are getting hot and both thermostats (Hallway and 1st floor) have been cross checked with other thermometers.
With an outside temp of about 8 degrees I noted following internal temperatures:
Hallway 17deg
Ist floor landing 18.5
I set the hallway stat to 20deg left the 1st floor stat at 18deg, and an hour later I checked the temperatures:
Hallway 19deg
1st Floor landing 19.5
The hall thermostat had not clicked out at all and the system had been running constantly for the hour.
I took a temp reading at the ceiling by the stairs: – 25 degrees!
Therefore it seems to me (IMHO) that most of the heat from hallway rad (2109 btu )is being funnelled up stairs and heating 1st and 2nd floor landings without being able to warm up the hallway sufficiently to trip the stat. This means the heating system is going constantly (and costing me a fortune).
The other downside is that to get any heat into the bedrooms (1st and 2nd floor) I have to have 1st floor stat set to 22/23deg!
This just does not seem right for a new build house, and I was wondering if any Heating Engineers on here could give their opinion.
Sorry it’s a long post, but I just wanted a 2nd opinion before I contact the builder
Thanks
I have just moved into a new built house and the heating seems ineffective so if any heating engineers could offer their opinion i would be very grateful:
House is 3 storey with 2 heating zones both controlled by thermostats one in hallway and one on 1st floor.
System is basically all working as it should, all rads are getting hot and both thermostats (Hallway and 1st floor) have been cross checked with other thermometers.
With an outside temp of about 8 degrees I noted following internal temperatures:
Hallway 17deg
Ist floor landing 18.5
I set the hallway stat to 20deg left the 1st floor stat at 18deg, and an hour later I checked the temperatures:
Hallway 19deg
1st Floor landing 19.5
The hall thermostat had not clicked out at all and the system had been running constantly for the hour.
I took a temp reading at the ceiling by the stairs: – 25 degrees!
Therefore it seems to me (IMHO) that most of the heat from hallway rad (2109 btu )is being funnelled up stairs and heating 1st and 2nd floor landings without being able to warm up the hallway sufficiently to trip the stat. This means the heating system is going constantly (and costing me a fortune).
The other downside is that to get any heat into the bedrooms (1st and 2nd floor) I have to have 1st floor stat set to 22/23deg!
This just does not seem right for a new build house, and I was wondering if any Heating Engineers on here could give their opinion.
Sorry it’s a long post, but I just wanted a 2nd opinion before I contact the builder
Thanks