Posted: Thu Feb 26, 2009 3:24 pm
by raydee
I have a potterton Lynx2 boiler about 14 years old - recently the system pressure drops and the low pressure light comes on - I refill system every 3 days or so
Water is escaping out of the overflow pipe - 1 litre/day
Can you suggest a fix and poss cost
Thanks [/code]

Posted: Fri Feb 27, 2009 6:50 am
by Steve the gas
Hi Raydee,

either the PRV valve is shot and/or the exp vessel.
To check EX Vessel - depress the car type valve on it - you should get air NOT water.


Hth

Posted: Fri Feb 27, 2009 7:03 am
by htg engineer
If the water is escaping when the pressure gauge is below 3 bar - then replace the pressure relief valve on the boiler.


htg

Posted: Sat Feb 28, 2009 11:52 am
by raydee
Thanks guys
I will test it out this week-end