Hot Water system mixing with Central Heating system - Help!

Posted: Sun May 27, 2007 2:37 pm
by DestroyItYourself
Hi

I have a low pressure heating system (gas boiler with hot water cylinder, vents, etc) and even though I have switched off the central heating on the control panel for the summer, the radiators heat up when the hot water system is activated.

My immediate suspicion is the the solenoid switch that directs the flow of hot water to each system. Even if I set it to "manual", it still heats up the radiators.

Any suggestions most welcome

Thanks

hot water mixing with circentral heating

Posted: Sun May 27, 2007 7:30 pm
by bazza
hi destroyityourself is it just the upstairs rads that are getting warm if so its gravity curculation you cud stop the problem by fitting a anti gravity valve bazza

Posted: Mon May 28, 2007 2:03 pm
by htg engineer
remove the actuator head and make sure the valve spindle moves freely, then try the actuator making sure it moves round when water, heating or both selected, sometimes the actuator head gets chewed where it sits on the valve, so even setting the actuator to manual the valve may not be turning.

Posted: Tue May 29, 2007 8:03 pm
by DestroyItYourself
thanks for your feedback so far