Posted: Mon Jan 11, 2010 3:53 pm
by Milpol1
Good day...............

I have a freind who se boiler is playing up, cant remeber the make sorry, however what is happening is that the pressure is going to zero, we have put water back into the system and the boiler fires up no problem, but then over night and after the boiler has been on for hours the pressure in the boiler goes down to zero again. Again it is filled and the same thing happens.

Any ideas what it could be please.
]
]Thanks in advance

Posted: Mon Jan 11, 2010 8:48 pm
by stoneyboy
Milpol1,
Most likely cause is that there is a leak in the system - find it and repair it.
end

Posted: Tue Jan 12, 2010 9:24 pm
by htg engineer
Keep an eye on the pressure gauge, if it rises to 3 bar with the heating on - then the expansion vessel needs re-pressurising or replacing.


htg

Posted: Sun Jan 17, 2010 8:47 am
by Steve the gas
Is the PRV dumping water outside?

Or have you solved this?