Potterton Kingfisher MF

Posted: Fri Jun 11, 2010 4:26 pm
by Emulated
My Potterton Kingfisher MF fires instanly on initial start up but once it has done a cycle of heating the hot water and whilst the boiler is still warm the relay clicks about 5 times and it takes several goes to fire up. I had the thermostat replaced but it made no difference.

Posted: Sat Jun 12, 2010 12:57 pm
by htg engineer
You need an RGI to check and adjust pilot, once the appliance is warm there's a better pull on the flue, a dirty or poor pilot the gas is pulled away from the pilot - so the gas air mixture isn't correct.


htg

Posted: Sat Jun 12, 2010 2:06 pm
by Emulated
Many thanks. Maybe the service man failed to understand the problem and simply fitted a new temperature control. I will ask him to recall and see how it goes.


htg engineer wrote:You need an RGI to check and adjust pilot, once the appliance is warm there's a better pull on the flue, a dirty or poor pilot the gas is pulled away from the pilot - so the gas air mixture isn't correct.


htg

Posted: Mon Jul 05, 2010 10:17 pm
by eggers
is it open flued mf or room sealed?
the air intake on the open flued mf do get clogged easily, but it could be a blocked pilot, or a flame rectification fault