Posted: Thu Mar 08, 2007 7:16 pm
by lavjohn
The pilot light on our boiler (BAXI BERMUDA 551) keeps going out, it runs fine when I relight it but every few days it goes out again.

Any suggestions as to anything I can do before I call in the professionals

Posted: Fri Mar 09, 2007 10:31 pm
by Eddy
Sounds like could be a couple of things. First (and probably most unlikely) is that it's being blown out by high /gusty wind. I once had a balanced flue boiler with short balanced flue through side wall and this used to happen often, but if it's a Baxi style, non-balanced, with vertical chimney-type flue this is very unlikely.

Much more likely is the thermocouple is getting tired. Cheap option would be to try replacing the thermocouple and see if that cures it. Not sure what this would be, probably around 5 to 10 quid but worth a try before calling the pros in, if you're happy working on the boiler?

Posted: Fri Mar 16, 2007 12:31 pm