Posted: Tue Oct 02, 2007 9:34 pm
by bazza
hi guys fitted an external expansion vessel on a baxi 105e but now wen i put the heating on the bar pressure on the gauge dosnt move it stays at 1 bar then after about 5 mins the boiler main burner goes out i teed the vessel into the return pipe close to the boiler wat hav i dun wrong n shud i fit a external prv n seperate warning pipe need advise as quick as possible THANX 4 any advise bazza

Posted: Wed Oct 03, 2007 4:54 pm
by htg engineer
Check automatic airvent is open.

Do the temperature lights go up to 70degrees ?

Does the flow pipe from the boiler get hot. and do the radiators heat up ?

Did you turn off the flow and return isolation valves ? are they fully open ?
and have you vented all radiators, pump ?

htg engineer

Posted: Mon Oct 08, 2007 11:32 am
by bazza
thanx 4 advise you were right the automatic air vent had bin closed off so i opened it n after a bit of rumblin it seems 2 be workin fine now ps sorry 4 late reply bin really busy cheers bazza