by Arabella0802 » Tue Sep 20, 2022 8:08 pm
by stoneyboy » Wed Sep 21, 2022 9:48 pm
by Arabella0802 » Wed Sep 21, 2022 10:55 pm
by ericmark » Thu Sep 22, 2022 3:52 am
by stoneyboy » Thu Sep 22, 2022 9:30 am
by ericmark » Thu Sep 22, 2022 11:42 am
by Arabella0802 » Sat Sep 24, 2022 8:09 pm
ericmark wrote:Most gas boilers are designed to modulate, i.e. turn down, they do this to keep the return water cool enough to allow the boiler to gain the latent heat from the flue gases.
If the radiators are set up correctly there will be with the TRV wide open about 15ºC difference in the temperature of water going into radiator and the water returning from the radiator, if some one has opened the valve on the other side of any of the radiators called the lock shield valve, then hot water will quickly return to the boiler, which will cause the boiler to modulate.
If all set correct then on switch on radiators will get hot, but it should take around 1/4 hour to reach full heat, as it takes a TRV around 5 minutes to cycle so if the radiator heats up too fast, the room temperature can over shoot.
What should happen is the TRV will regulate the heat in an analogue manor, not on/off, but gradually opening and closing to maintain temperature it is set at, so radiators should cool down once room reaches temperature but not switch fully off, just warm enough to keep room at set temperature.
So once the heating has been running for a time, if radiators go hot then cold then hot etc, there is something wrong, they should just stay warm.
The boiler will adjust output to match the demand from the TRV's once it can't turn down any more then it will start cycling off/on to further reduce output.
There should either be a modulating wall thermostat which turns boiler up/down, or in a room normally kept cold a on/off thermostat to turn off boiler on warm days, under normal winter running the wall thermostat should not turn off, if it does you get a temperature hysteresis, but if the temperature is controlled by the TRV then you don't get the hysteresis.
The problem is mechanical TRV heads are often marked *123456 rather than in degs C, and so it is a bit of guess work setting temperature, electronic types do show degs C and can be set to adjust room temperature according to the time of day.
by stoneyboy » Sat Sep 24, 2022 9:59 pm
by Arabella0802 » Sat Sep 24, 2022 10:53 pm
by stoneyboy » Sun Sep 25, 2022 1:26 pm