radiator not working
Posted: Sun Jan 20, 2008 11:18 pm
by kerry watkinson
why is one radiator cold when all the other radiators in the house are hot and working correctly?
Look forward to hearing from anyone who can help.
Kerry
Posted: Sun Jan 20, 2008 11:37 pm
by rosebery
1. Has it got air in it? Try opening the bleed vent.
2. If you have standard valves is the flow open? If it's not then no hot water will get in.
3. Have you got a TRV on it? - It might be stuck and no hot water is getting in.
Try checking those to start with.
Cheers
Posted: Mon Jan 21, 2008 3:58 pm
by roger196
Having tried the advice of rosebery, if the rad is still cold, there is air in the pipes leading up to this rad. To shift this keep the CH on and gradually turn off all the other rads except this one and one other. This should work just by turning off the adjustable valve on each rad. But if you close the lockshield valve as well, make a note of the number of turns you close. This will enable you to restore the balance of the system afterwards.
radiators
Posted: Sun Jan 27, 2008 4:53 pm
by florence1
[quote="rosebery"]1. Has it got air in it? Try opening the bleed vent.
2. If you have standard valves is the flow open? If it's not then no hot water will get in.
3. Have you got a TRV on it? - It might be stuck and no hot water is getting in.
Try checking those to start with.
Cheers[/quote]
Dear Rosebery,
How do you shift the valve if it is stuck?
When I unscrew the cap I find a pin - do I try to turn it?
Thanks Florence1