Overflow Pipe

Posted: Sun Feb 17, 2008 8:14 pm
by Tanya82
Hi

Can anyone give m e a clue as to what is going on with my overflow pipe - I have noticed in the last few weeks that the overflow at the front of my house keeps dripping in the evening (there is a couple of pipes).
This morning it was so icy I nearly fell over it, so I have looked on here and gone out and felt the water - it is warmish, but can't find the reason it is dripping.

Can anyone give me an idea, do I need to get a plumber or is it something I can do myself - like changing a ball?

Any help is appreciated, Tanya

Posted: Sun Feb 17, 2008 8:35 pm
by htg engineer
what type of heating system do you have - if you don't know - what's the make and model of the boiler.

Posted: Sun Feb 17, 2008 8:43 pm
by keitht
if the water is warm sounds like the heating is pumpin over therefor fiilin the header tank

Posted: Sun Feb 17, 2008 10:59 pm
by Sparkgap
Is this a sealed system (boiler fed off the mains, no tank in roof)? Have you topped up the boiler recently? If yes it could be your expansion vessel inside the boiler. Had a similar problem with mine which I thought was due to leakage from the heating system and topped up from the mains, then overflow/safety valve started dripping. Because air had leaked out of the expansion vessel as the system warmed up and water expanded there was nowhere for it to go except out the safety valve. Got bike pump and put more air in expansion vessel and all okay.