by htg engineer »
Tue Mar 11, 2008 8:44 am
Do you mean new 3 port valve or actuator head was replaced ?
What happens if you put HW only on ? do the rads heat ?
Turn on CH and HW, leave for abit to allow it to heat up - go to the 3 port valve all 3 pipes should be hot, if the HW one isn't then the actuator isn't turning.
Remove the actuator/motorised valve, and select hot water only, and see if the D shaped aperture turns. Then select water and heating. If it's not turning then that's the fault, if this is what was replaced - then it could just be a loose wire. If it wasn't replaced i would replace it.
If the system was drained to fit a new 3 port valve - then there could be an airlock.