penetrating the tanking with pipe work

Posted: Tue Mar 15, 2011 10:36 am
by Boudicca
This is a concern my building officer has brought up in his latest letter, could someone advise on this subject? :(
Considerable concern is expressed regarding the tanking provisions provided to the external walls, the membrane sheet has not been fixed in accordance with any manufacturers details and appears to have been fixed to an insulation board in the cavity which is not an acceptable detail. Tanking must be a continuous fully supported fixed barrier with full continuity maintained. The work does not appear to meet the minimum requirements of the building regulations and cannot be approved by building control. A also note that drainage from the proposed ground floor bathroom will penetrate the tanking, any penetrations must be carefully detailed to prevent damp penetration. I strongly suggest that you seek specialist advice and seek a way forward on this matter. I strongly advise against proceeding with any finishing/ plastering work before this matter has been resolved.

damp

Posted: Wed Mar 16, 2011 5:20 pm
by welsh brickie
he will not sign off your build as it has not passed the requirements set by the local authority,
He wants a specialist contractor to provide a report on how the damp proof membrane is installed and details of how to seal pipework through the wall.
As him to come round and explain exactly what he wants face to face.