Earth bonding at gas meter

Posted: Tue Apr 24, 2007 8:36 am
by Lee the novice
Hi all,

I have a contract for the house with BG. On their inspection they say the earth bonding is on the wrong side of the gas meter (it was on the pipe that went into the ground). On asking him he said it should be between the meter and the house and be within 600mm of the meter.

I bought a new earth strap and moved the original earth wire to the house side of the meter, it's before any joints and within 600mm.


Is this correct???

gas metre bonding

Posted: Tue Apr 24, 2007 8:29 pm
by Jeffmo
sounds ok , but make sure it is 10mm earth wire and make sure the contact surface of pipe to clip is clean . Also remember you shouldn't be doing it . Naughty naughty. Regards Jeff. PS get a qualified leckie to check all bonding its important to save your life

Posted: Tue Apr 24, 2007 8:49 pm
by sparx
yessir as long as it's after flex pipe

Posted: Thu Apr 26, 2007 7:09 am
by Lee the novice
Many thanks