Posted: Sat Apr 28, 2007 9:25 am
Hi All
New to the industry with a dilema.
Customer is having the meter box moved which will mean I will need to lengthen the tails by approx. 1metre (total 2M). Original cable is 25mm on a 100 amp 1361 fuse.
Builder wants to run the 25mm tails in the cavity which is allowable under building regs however this does not account for cavity wall insulation in the future which would derate the cable by 0.5 and therefore make the current carrying capacity of the cable too low. But then this is probably the case for 90% of the houses in the uk. Indeed my own house has 16mm tails with an assumed diversity of 40Amps and supplied via a 60Amp 1361 fuse. Derating this by half would mean altering the cable size to 70mm as indicated in Table 4D1A. which would be impossible to terminate in my tiny consumer unit. So a bit of consideration needs to go into how likely the cable will be overloaded and for how long.
Would it be advisable to drop the incoming fuse to 80 amps (from 4D1A 25mm cable ref method 4 will carry 80 Amps) and crimp join the new 25mm cables running to the new box position. If so, can I use heat shrink to protect the cables.
New to the industry with a dilema.
Customer is having the meter box moved which will mean I will need to lengthen the tails by approx. 1metre (total 2M). Original cable is 25mm on a 100 amp 1361 fuse.
Builder wants to run the 25mm tails in the cavity which is allowable under building regs however this does not account for cavity wall insulation in the future which would derate the cable by 0.5 and therefore make the current carrying capacity of the cable too low. But then this is probably the case for 90% of the houses in the uk. Indeed my own house has 16mm tails with an assumed diversity of 40Amps and supplied via a 60Amp 1361 fuse. Derating this by half would mean altering the cable size to 70mm as indicated in Table 4D1A. which would be impossible to terminate in my tiny consumer unit. So a bit of consideration needs to go into how likely the cable will be overloaded and for how long.
Would it be advisable to drop the incoming fuse to 80 amps (from 4D1A 25mm cable ref method 4 will carry 80 Amps) and crimp join the new 25mm cables running to the new box position. If so, can I use heat shrink to protect the cables.