Supply for shower pump

Posted: Sat May 24, 2008 6:33 pm
by morganpj
Hi,
I have a shower pump and need an electric supply to it. The pump will be in the airing cupboard and there is electricity there for the heating controls, timer, water pump, emersion heater etc. Would it be OK to take a spur off the heating junction box? Any advice would be appreciated, Thank you.

Posted: Sun May 25, 2008 12:26 am
by rosebery
Using the CH / DHW wiring centre is not on.

There is no reason (that I can see) that you shouldn't take a spur off the immersion heater supply which should be quite separate from the wiring centre.

Cheers

Posted: Sun May 25, 2008 10:18 am
by morganpj
Thank you Rosebery. I had a look at the immersion heater switch and thought at the time that this also was connected to the CH and as you say seperate from the wiring centre. I pulled the fuse in the CU for the upstairs sockets and the immersion switch was still live when tested. I believe that this switch is connected up to the CH fuse which is 15amps. Is it still OK to spur off this switch? Any further advice please. Thank you.

Posted: Sun May 25, 2008 10:03 pm
by ericmark
In theory no. Supply to immersion heater should not feed anything else.
In practice I would, and use a switched fuse spur with correct fuse for pump. Most likely 3 amp.