this question arises when wishing to feed a central heating boiler system from an immersion heater supply as it is very unlikely to be supplying both together.
The regs book gives 3 'standard domestic circuits' to save us having to work out the loadings etc. ie Ring[A1], 32A 4mm2 radial [A2], & 20A 2.5mm2 [A3] radial.
We are totaly at liberty to design other non-standard circuits as long as if questioned we can show design parameters worked to, this of course is normal non-domestic practice.
The point you are looking at is if say a 16A mcb is used to supply even 4 radials from its origin at the board could you overload any part of any wiring & the answer has to be no! The total load you could impose on all or any of the cables would be 16A before the CB tripped. This is IMHO not a problem if no other choice easily available, as long as you feel happy to 'defend your corner' if questioned, I have lost count of the times I have seen 2 lighting cables put together on one 6A cb to free off a space in Con. unit for a shower etc.
regards