PLASTIC PATRESS BOX, METAL SOCKET PLATES
Posted: Sat Aug 02, 2008 11:12 am
by ANDREW KNOX
I have plastic patress boxes in stud wall; can I change the sockets with metal ones.??
Andrew
Posted: Sat Aug 02, 2008 5:22 pm
by kbrownie
ANDREW KNOX
Metal sockets fronts will fit on to plastic boxes, remember to connect the earth cable to the metal socket front earth terminal.
Regards
KB
Re: PLASTIC PATRESS BOX, METAL SOCKET PLATES
Posted: Sat Aug 02, 2008 5:30 pm
by BLAKEY1963
[quote="ANDREW KNOX"]I have plastic patress boxes in stud wall; can I change the sockets with metal ones.??
Andrew[/quote]
ANDREW KNOX
If the existing r cavity dry lining boxes , then metal
can be used , with noggins of wood for support.
If metal face plate sockets r used then it is vital
that they r properly earthed to the c.p,c of the ring main circuit
BLAKEY1963
Posted: Sat Aug 02, 2008 7:38 pm
by ANDREW KNOX
Thanks Blakey
Perhaps my question should have been: How do I ensure that metal socket plates are earthed correctly. Yes, they are dry lining plastic boxes set in the plasterboard so there's no earthing point in the corner like with metal boxes.
Thanks again
Andrew
Posted: Sat Aug 02, 2008 9:21 pm
There has been many posts about earthing of back boxes and it is considered by many not to be required as if metal they would be earthed by the 3.5 mm fixing screws. So in your case so long as the earths are connected to the socket there should be no problems.
As how to ensure earthed correctly we use a meter called an earth loop impedance tester which draws heavy current Live to earth for few milliseconds and calculates with the volt drop what the total resistance of cable from supply transformer to socket and back is and is referred to as Zs.
Because these meters are expensive and can cause danger when used they are normally only used by electricians.
Assuming on a ring main measuring between both earth wires is normally a good indication. 1.4 ohm is the maximum Zs reading considering the supply to house can be 0.35 I would consider 1 ohm between both earth wires as max.
Does this answer your question?
Posted: Sun Aug 03, 2008 2:37 pm
by ANDREW KNOX
Thanks everyone,
So it looks like as long as I make sure the earth cable in my ring main cable goes into the earth connector and is properly sheathed I'll be OK
AK