by ericmark »
Tue Sep 09, 2008 10:25 pm
I will try to take you step by step but please ask if I lose you on the way.
1) In the British regulations called BS7671:2008 you are allowed up to 16 amp to lighting circuits 559.6.1.6 but also manufacturer’s instructions must be complied with 559.4.1 and 134.1.1 and most ceiling roses are rated at 6 amp so as a result in the main 6 amp is the largest overload (MCB/RCBO) or fuse we can use. And with this in mind I am very surprised that the manufacturer of this luminaire has recommended a 10 Amp protection device.
Now I will try to explain the difference between a fuse and MCB/RCBO. A fuse will blow at the rated amps but only after a long time. And graphs and charts are produced to tell us how much extra current is required to make a fuse blow in a set time. A 13 amp fuse as found in a standard 13 amp plug needs 95 amp to make it blow in 0.4 seconds. And when an electrical circuit is designed we have to plan for this and we calculate or measure the earth loop impedance to ensure if there is a fault that the fuse will blow in time not to injure a person. This is what limits the length of cable that can be used.
With MCB/RCBO devices however there are two or three independent systems to trip the device and for a long period of overload it uses a thermal device but for short period overload it uses a magnetic trip. This magnetic trip will allow 3 to 5 or 5 to 10 or 10 to 20 times the rated current to flow for a very short time and are given letters B, C, and D. So a B6 MCB will trip at 30 amp even if it only flows for 0.08 of a second (Two cycles) a C6 with trip at 60 amp and a D6 at 120 amp.
I have not got the details for a 5A BS 1362 fuse but at 0.1 seconds looking at something like 30 A and at 5 seconds 14 A. Although it would seem it acts just a quick as a MCB because the inrush for both bulbs and transformers takes place in first milliseconds fuses do not tend to be so affected by inrush as a MCB.
Back to reality changing the B6 to a C6 or D6 will likely cure the problem but before doing this one must be sure the circuit will trip in time if the MCB is changed and the meter used to measure EFLI is expensive plus to change the MCB will require alteration within the consumer unit. Because it could cause danger the government introduced Part P which means it will cost you more to DIY than to get a registered electrician to do the job. Who will issue certificates you will need if you ever sell your house.
I know this seems complex and this is why Part P was introduced. I don’t like Part P but I can’t ignore it.
Eric