Page 1 of 1
Moving Boiler
Posted: Thu May 10, 2007 9:26 pm
by McT
I'm having my boiler put in the loft. The power to it at the moment comes from a single 1.5mm cable straight from a Wylex NN916 consumer unit on its own NB15 15A Type 2 breaker. When it is moved I would like to add some extra sockets - 1 for a whole house pump, 1 for an aerial booster and a couple for anything else, e.g. Sewing Machine, Computer etc. What is the best way of achieving this.
Posted: Fri May 11, 2007 6:13 pm
by sparx
A you have a radial on a 15A mcb then there is no reason why you can't extend it to several sockets as long as you realise the limit of load, as boiler system usually only requires a 3A fuse, leaves nominal 12 A for other loads this equates to almost 3 kWatts so your proposal is reasonable although power circuits normally wired in 2.5mm as long as mcb not uprated no probs.
If boiler being moved it might be a good time to upgrade circuit to 2.5 on 20A mcb then as above but higher load now poss. ie blr, plus 4kW.
Regards SPARX
Posted: Fri May 11, 2007 7:32 pm
by McT
Thanks - I was thinking of just changing to 2.5mm cable and leaving the breaker at 15A. These mcb's are not that easy to obtain, and since the load is quite low, I think 15A is plenty?
Posted: Sat May 12, 2007 10:43 am
by sparx
Good move! It's surprising how little we actually use due to diversity of load,
regards SPARX