Zone 0 basically inside the bath, zone 1 goes up to 2.25meters, zone 2 goes out horizontal 0.60 m from zone 1 there is another horizontal limit of 3 meters from zone 1 before socket outlets can be fitted which is really for when one fits a shower in a bedroom.
Anything in Zone 1 and 2 needs to be IPX4 and regulation 701.411.3.3 needs RCD protection for all circuits.
Where the location containing a bath or shower is in a building with a protective equipotential bonding system in accordance with Regulation 411.3.1.2, supplementary equipotential bonding may be omitted where all of the following conditions are met:
(i) All final circuits of the location comply with the requirements for automatic disconnection according to Regulation 411.3.2
(ii) All final circuits of the location have additional protection by means of an RCD in accordance with Regulation 701.411.3.3
(iii) All extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2.
NOTE: The effectiveness of the connection of extraneous-conductive-parts in the location to the main earthing terminal may be assessed, where necessary by the application of Regulation 415.2.2.
Also if you read Best Practice Guide 1 at
http://www.esc.org.uk/business-and-comm ... uides.html this may help on earth question for lights.
Inspections are normally carried out in stages called normally first and second fix. You should have an inspection before you tile. The Part P when done by the council seems to be a little open as on one hand it is suppose to follow BS7671 which means the person responsible for site safety i.e. LABC should inspect as the job progresses and issue an installation certificate but it also states under Part P the LABC will not issue an installation certificate only a completion certificate.
As electricians the problem does not arrive as we write out the installation certificate it is only an issue with the DIY man as a result don’t really know how this problem should be addressed.
It is normal to run fans from lighting to make the switching on and off with lights easy but as an alternative duel pole lighting switches can be used so electrical separate but switched together. Some fans require a max of 3 amp fusing and the alternative method is only real way to fuse down to 3 amp rather than normal 6 amp used with lighting.
I am lead to understand one should submit all this to council when applying for Part P but a recent discussion on a professional forum seems to say the councils are not following the legal requirements and in many areas Part P as run by the councils has become a farce. Including councils charging extra fees for inspections for which they should foot the bill. But of course since this is only a problem with DIY people who in the main don’t know what the council should be doing for their money the councils are getting away with it.
There is a link to Part P in projects area if you haven’t already down loaded a copy I would do. It may save you some money. It has not been up-dated since June so for forms go to
http://www.theiet.org/publishing/wiring ... /index.cfm you can download BS 7671:2008 forms which are up-dated and haven’t got “On line edition” printed all over them.
Normally I would have waited for your reply but since Christmas not sure when posts will be cleared so thought I should give a little more info without waiting for request.
Merry Christmas Eric